Originally Posted by KeepItSimpleStupid
Since you have a pool, that creates lots of problems. I's might initially assume that nothing is wrong, however I would d the following:
THE POOL IS ON ITS OWN BOX AND METER AND SEPARATE FROM THIS. I MENTIONED
IT AS AN EXAMPLE OF WHAT I DON'T SEE. THERE IS NO TRANSFORMER GROUND. THE METER ON THE HOUSE IS IN SERIES WITH THE MAIN (ONLY) TRANSFORMER, AND THE ONLY GROUND I CAN GUESS AT IS COMING BACK INSIDE THE PANEL TO THE METER...BUT I can't OPEN THE METER TO SEE IF IF IT REALLY GOES INTO THE PVC PIPE TO THE GROUND.
1. Replace switchplate with a plastic one. Decora style switches might be an option. Really concerned replace the metal screws with nylon.
SWITCHPLATE IS PLASTIC ALREADY, CURRENT IS FROM SCREWS ONLY. WILL LOOK FOR NYLON.
2. Power circuit from a GFCI breaker.
I COULD BUY ONE FOR THE WHOLE GARAGE, BUT IT SEEMS CERTAIN IT WILL TRIP
IF GROUND IS ALREADY HOT (WHAT AM I MISSING?).
Now to address the ground problem.
1. Is there a separate neutral and ground bus in your main panel. If so, the ground may be at the transformer or at the meter disconnect, if you have one.
YES, IN FACT THEY ARE SEPARATE IN THE GARAGE MAIN PANEL AND 220V BREAKER GROUND WIRES ARE ON BOTH NEUTRAL AND GROUND BARS...BUT FROM WHAT I READ IF THERE IS A MAIN DISCONNECT IN THE PANEL (WHICH THIS GARAGE PANEL HAS) THEY ARE MARRIED AND THIS IS IRRELEVANT (PLEASE DISPUTE...I THOUGHT THIS WAS WRONG AT FIRST).
2. There has to be a ground somewhere.
AGREED. BUT IN MY MUDROOM WHY DOES IT SEEM TO BE FEET?
1. Outside disconnect (ground an neutral will be separate)
IT WOULD APPEAR THIS PANEL IS SECONDARY TO THE MAIN HOUSE PANEL WHICH FEEDS BOTH THE INSIDE HOUSE PANEL AND THE GARAGE PANEL.
NEITHER HOUSE PANEL HAS A MAIN DISCONNECT, BUT THE 200A PANEL IN
THE GARAGE DOES.
2. Main panel (ground and neutral will be separate)
THEY ARE SEPARATE IN THE GARAGE PANEL AND MIXED WITH 220V GROUND WIRES
ON THE NEUTRAL AND GROUND BAR WHILE THE 120V ARE ON THE GROUND BAR ONLY...BUT THE MAIN
DISCONNECT IN THIS PANEL IS SUPPOSED TO MAKE THIS NULL (?).
3. At transformer
I SEE NO GROUND THERE...WAS HIT BY LIGHTNING LAST YEAR WITHOUT ANY RAIN
WHILE I WEEDWHACKED A FEW FEET AWAY...LIKE A BOMB...THEY RESET IT AND REPLACED SOMETHING SMALL THAT TOOK THE CHARGE...NEVER SAW A DOG MOVE SO FAST IN MY LIFE.
3a. Ground and neutral may or may not be separate
RIGHT...DO I POWER UP THE PANEL WITH THE COVER OFF AND START FINDING OUT?
IS IT POSSIBLE THE BARS ARE NOT CONNECTED? WHY WOULD THE BREEZEWAY LIGHT ONLY LIGHT WITH BOTH SWITCHES ON INSTEAD OF EITHER?
Usually there is a ground at the transformer and the house. The pool should have it's own rod because it is detached.
I'M GUESSING THE GROUND AT THE POOL IS FROM A WIRE INSIDE THE POWER CORD TO
THE SPA HEATER OR PUMP...AND THAT EFFECTUALLY DOES THE WHOLE PANEL (?).
THE WATER PIPE ENTERING THE GROUND IS PVC.
Ground can be a water pipe, but you ruled that out.