I have a 3 1/2 year new AMANA GUIV070FX40 attic mounted system that is the furnace / air handler for an AMANA RCE42C2A condenser / compressor. The entire system, including new ducting and separate electrical circuits (220 for the compressor / 110 for the air handler) was installed by a credible / licensed contractor who has since retired... the air handler blower quit 2 days ago. Both circuits have been reset and metered for correct voltage. The compressor runs fine with good refrigerant charge and if allowed to run while the air handler blower isn't working, the condensation on the refrigerant lines will freeze in fairly short order. There is only a single flash of the diagnostic LED on the PC board in the blower compartment after cycling the power, then all LEDS go out and remain out. The air filter is brand new. The air handler blower motor is mechanically free to rotate with no noises or binding and will NOT come on by the manual switch selector or from the heat side or cool side of the thermostat. The thermostat temperature selector WILL drive the compressor to start on the cool side and WILL drive the heater burner to activate on the heat side --- the air handler blower still doesn't come on. As this blower motor is a variable speed (ECM) type, I haven't been able to find a starter or condenser. I don't see any reset button on the PC Board. Is there any way to test for voltages on the PC Board to confirm whether the Board or the Blower is at fault?
Add'l info: 110VAC to blower motor confirmed good by multi-meter... both power and control line(s) plugs removed, inspected and re-seated @ both the motor and PC Control board... 24VAC @ low-voltage xfmr confirmed by multi-meter. There is no capacitor or inductor in the blower motor 110VAC circuit.