I have a refrigertion unit that is not working properly. First there was a problem with the solenoid valve and then a compresser replacement. Unit is still not working. The pressures with unit runnig is 4 psi suction and 200 head, R-22. Unit has plenty of refrigerant because unit is running as the safties are all closed. The compresser does not run hot it is rather comfortable to the touch. I believe the TXV is the culprit. Testing the sensing bulb with hot and cold water should this be done with the unit on?