    Goodman cpke 30-18 control issue
    I Have a goodman heatpump/air conditioner and the inside blower does not come on causing the compressor to ice up. If I play with the blower controles then it comes on but a few days later it happens again. Only in Air not heat. I replaced the controls (thermostat) no joy.. any help?
  • Jun 15, 2008, 10:35 AM
    hvac1000
    If I play with the blower controls then it comes on but a few days

    Check for loose wiring. It could also be a intermittent blower relay.
  • Jun 19, 2008, 12:58 AM
    cliff28570
    Thanks I found a connection or splice about 2 feet from the compressor which I took it that they had cut the cable too short. I removed the tape ( fuse removed) and took the wire twist cap off to find that the red wire was badly corroded. Cleaned it up and no problem since. Thank you very much you have saved me some serious bucks.
  • Jun 19, 2008, 05:35 AM
    hvac1000
    Always glad to help.