  • Jun 13, 2008, 10:33 AM
    badady1
    Wiring a 3 prong plug to a 4 prong outlet
    In my Laundry room I have a 4 prong plug for my dryer. I have a 3 prong plug on my welder. They are both 220 and I have everything I need to make an extension cord in cluding wire, plug and receptacle and gang box. I know how to wire the ground but am not sure where to put the black and white wires. On the three prong plug does it matter which side they go on? There is a wider prong on one side of the receptacle. On the 4 prong plug I will be excluding the fourth prong. Does it matter which side the white and black go on? Thank you
  • Jun 13, 2008, 11:01 AM
    donf
    Badady,

    What is the amperage of the dryer? What is the amperage of the welder?

    By the way, there is no longer a 220 VAC. The current VACs are 120 and 240.
  • Jun 13, 2008, 12:06 PM
    stanfortyman
    I can only assume the dryer is a 30A circuit. Unless your welder can run on a 30A circuit forget it.

    As Don said, there is NO "220" any more. Hasn't been for a very long time, we just can't shake the misnomer. Also, this is only HALF the equation. You also need to know the amperage of the circuit.

    A typical electric dryer is a 120/240v-30a circuit. Your welder needs a straight 240v circuit hence the different 3-wire and 4-wire devices.
  • Jun 13, 2008, 12:06 PM
    badady1
    Quote:

    Originally Posted by donf
    Badady,

    What is the amperage of the dryer? What is the amperage of the welder?

    By the way, there is no longer a 220 VAC. The current VACs are 120 and 240.

    My Dryer does not have an amperage written on it, My welder is 208.
  • Jun 13, 2008, 12:09 PM
    badady1
    Sorry guys,
    The Dryer is on a 30 amp circuit. The weder is a 205 max amp
  • Jun 13, 2008, 12:10 PM
    stanfortyman
    No, not the output amps, the input amps.
  • Jun 13, 2008, 12:14 PM
    badady1
    230/220 volts
    47.5 Amperes
  • Jun 15, 2008, 12:29 PM
    stanfortyman
    Quote:

    Originally Posted by badady1
    230/220 volts
    47.5 Amperes

    And you want to know if you can use this on a 30A circuit??
  • Jun 16, 2008, 08:59 AM
    badady1
    Yes
  • Jun 16, 2008, 09:15 AM
    donf
    It's an emphatic, NO!

    You would need to run a #6/3 AWG on a 60 amp breaker for the welder.
  • Jun 16, 2008, 09:40 AM
    KISS
    Sorry Don, I have to disagree.

    O come on. You certainly can. There will just be a limit as to what you can weld. I've connected a welder once for a temporary job. This thing was like 4' x 3' x 2'. A huge welder. Just pulled the wires out of the wall. Wirenutted it in place. The circuit was no where what was "required" for the welder. Worked fine to weld 1/4" stainless tubing.

    You will not use the N terminal on the 4 wire plug. It doesn't matter which one of L1 and L2 gets connected to the other terminals. You know where ground goes.

    There are terminal designations on the back with a white, black, red and bare wire connected to it. Don't use the terminal with white on it. The black and white of the welder cord go to black and red of the plug. It doesn't matter which one goes where.

    As long as you realize that there will be limits as to what can be welded, everything will be fine.

    So, if it's a 200 amp welder, it's now a 30/47*200 anp welder or a 127 amp welder.
  • Jun 16, 2008, 05:12 PM
    stanfortyman
    Yeah, but KISS, this is NOT smart advice to give on a public forum.
    Sure it can be used, but is it right? NO. Is it safe? Maybe.
  • Jun 16, 2008, 06:16 PM
    badady1
    I wired it with a 4 prong plug. Eliminated the second ground prong. Wired it with #10 wire to a 3 prong receptacle inside of the gang box and it seems to be running the welder just fine. What's the deal? Did I just get lucky or what? It is on its own designated circuit.
  • Jun 16, 2008, 08:14 PM
    KISS
    Hopefully, you eliminated the neutral (white) and not the ground (bare).

    Your welder is just smaller now because of the circuit rating. No big deal.
  • Jun 17, 2008, 05:45 AM
    badady1
    Yes. The ground to the three prong plug is wired to the ground in the four prong plug.
  • Jun 17, 2008, 07:25 AM
    donf
    Keep your fire insurance payments up. You might need it, providing that the insurance company does not choose to drop you if you have a fire.

    BTW, I thought we were not allowed to give out information that we know to be unsafe.