Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Air Handler Trouble (https://www.askmehelpdesk.com/showthread.php?t=226212)

  • Jun 12, 2008, 04:06 PM
    mschumpert
    Air Handler Trouble
    I posted a few weeks ago about a buzzing I get from my air handler and apparently haven't figured out what is wrong yet. It will start up and then after several minutes start slowing down while a buzz increases in volume until the motor stops. It spins freely when off, but has resistance when on. The outside unit continues to run even when handler will not.

    My unit is a Carrier 40AQ030300SU

    First, I replaced the capacitor... same problem

    Then I noticed the sequencer? Was buzzing so I replaced it.

    Now I figure all that's left is the motor, but I had it replaced just last summer.

    However when I was looking at it it seems a wire coming of the sequencer looks like it should have a connecting wire to the motor but it does not. It comes from #6 on the sequencer and was just hanging there. Is this the wrong motor and thereby may be overheating? It is an Emerson ka55-hx-smr (it's a little blurred already so that's a guess.)

    If the motor is bad, what should I replace it with? Or do you think it's something else? Thanks!
  • Jun 12, 2008, 05:27 PM
    T-Top
    Did you replace the run capacitor when you replaced the motor? 1 motor may need a different size capacitor than the other even if it's the same horse power. High amp draw on the motor will make other part start to chatter and burn out.

  • All times are GMT -7. The time now is 01:36 AM.