-   -   Central ac coils freeze up and then blower motor quits (https://www.askmehelpdesk.com/showthread.php?t=225722)

  • Jun 11, 2008, 11:18 AM
    loneposse
    Central ac coils freeze up and then blower motor quits
    I have a problem with my Miller 2 ton central A/C unit,when turned on it will run for a few minutes then the coils etc start icing up fast and the blower motor will quit and get very hot.I have replaced the capacitors,contactor,cleaned coils & tried another blower motor but get the same results,the unit is a late 80's model.. any clues on what might be causing this? Thanks!:confused:
  • Jun 11, 2008, 11:24 AM
    crystalbivens
    You need to turn the unit off and let it thaw out then call a AC man to put some freon in it.
  • Jun 11, 2008, 11:27 AM
    hvac1000
    It could be a
    Undercharge of refrigerant.
    Plugged air filter
    Blocked return air
    Closed registers

    The blower motor should stay running all the time the A/C outside unit is running.

    The blower motor you replaced the original with could be defective.
    The blower motor could be running in the wrong rotation/direction causing the air not to move.
    Try running the blower motor by itself when the coil is not iced up. You should feel a strong flow of air out of all the registers.
  • Dec 3, 2011, 03:52 PM
    asopao20022002
    It could be the time delay ralay, replace it and see what happens! I am almost sure that's the problem.