    240V Table Saw
    Is there a correct way to connect a 240V table saw with a 15 amp 6-15 plug to a 14-30 125/240 outlet?

    If so would I tie the nutral & ground together or just use one or the other?

    Also should I add a separate in-line 15 amp breaker?
  • Jun 3, 2008, 01:06 PM
    KISS
    Simple enough. Just get a 2-pole fused disconnect, connect one end ( 3 wires, Ground, L1 and L2) of the proper AWG for 30A and connect it to a 6-15 socket.

    Use fuses rated for 15A. Use 3 wires (ground, L1, L2).

    If the outlet is not used, then you can change the receptacle and existing breaker.
  • Jun 3, 2008, 03:04 PM
    Dwall174
    Quote:

    Originally Posted by KeepItSimpleStupid
    Simple enough. Just get a 2-pole fused disconnect, connect one end ( 3 wires, Ground, L1 and L2)

    Thanks!
    That's what I thought, but I wasn't 100% sure on using the ground or nutral wire!


    Quote:

    Originally Posted by KeepItSimpleStupid
    If the outlet is not used, then you can change the receptacle and existing breaker.

    Yea the outlet is used for a dryer!