  • May 31, 2008, 06:18 PM
    ksmnrs
    Central air conditioner
    The above {heat pump} unit will run outside but the blower will not kick in on the inside. What could be the cause
  • May 31, 2008, 07:46 PM
    T-Top
    You need to check to see if you are getting 24v from the thermostat to the G circuit at the blower unit(blower relay or control board) Will the blower run if you turn the fan switch to on at the thermostat?
  • May 31, 2008, 07:48 PM
    hvac1000
    Bad bower motor
    Bad blower relay.
    If the blower motor will start by hand(CAUTION BE VERY CAREFUL) and runs it could be the capacitor for the motor.