OK, ac unit {trane}worked fine for the first couple of days except contactor had a buzzing sound louder than normal. One day, out side unit wouldn't kick on just loud buzz from contactor. I purchased a new contactor and the smaller capacitor, contactor was kicking in, still nothing only a slight humm. So I did some reading on this wonderful web sight and started checking all my volts. Discovered I was only getting 110 off one side of disconnect , the other side had a low voltage. The disconnect breaker was bad, so luckily I had a 60A breaker and installed it. Went in and turned on stat looked out side, the fan is blowing on ac unit. I thought Sweet! anyway noticed the compressor is not kicking in. both sides of the contactor are reading 115v, one side of the smaller capacitor is reading right side 215v the other side reading115, the bigger capacitor reading right side 115v and the left side reading 140v. Could this breaker going bad cause damage to something else? Maybe the larger capacitor? The hvac store is closed today.my guess is the bigger capacitor is bad or maybe low on freon.