Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Heating & Air Conditioning (https://www.askmehelpdesk.com/forumdisplay.php?f=150)
-   -   Thermostat wiring hunter 4 wire (https://www.askmehelpdesk.com/showthread.php?t=220909)

  • May 28, 2008, 08:03 PM
    bridgetmurr48
    Thermostat wiring hunter 4 wire
    I need help wiring a 4 wire system red green blue and white. I am trying to wire a hunter thermostat and have a forced gas furnace/ac unit. I put red to rh with a jumper from rh to rc and green to g and white to w and blue to Y1. It will not work. Please help any info would be appreciated. It is getting hot and I need to get the air to come on. Thanks
    Bridget
  • May 29, 2008, 02:09 AM
    hvac1000
    First
    Did you write down where the old wires came off the old thermostat terminals? If so follow the install manual that came with your new thermostat.
  • May 29, 2008, 02:51 AM
    KISS
    With 4 wires, you can figure it out. I recommend turning of the furnace between each trial.
    Connect only two wires at a time and figure out what turns on:
    1. Fan
    2. Heat followed by Fan within a few minutes
    3. Just the outside AC unit
    4. Nothing

    RED GRN BLU WHT
    0 0 1 1 ?
    0 1 1 0 ?
    1 1 0 0 ?
    1 0 1 0 ?
    1 0 0 1 ?

    So fill in the table with the proper number 1-4 and we'll figure it out. If nothing comes on, then there is a problem with the transformer or small fuse in the furnace.
  • May 29, 2008, 05:32 AM
    wmproop
    Its probably the thermostat,, after 15 years I have yet to run across a hunter tstat that was worth the space it takes up in the garbage can