-   -   Blower comes on 5 minutes after ignition (https://www.askmehelpdesk.com/showthread.php?t=220517)

  • May 27, 2008, 06:10 PM
    Alfred Ament
    Blower comes on 5 minutes after ignition
    I still having a blower delay on my Tempstar furnace after burners are on for 5 minutes!

    We have no Fan limit onli limitswitch !
  • May 27, 2008, 10:48 PM
    hvac1000
    Your burner might be out of adjustment not allowing enough gas through to heat the unit up quickly. The furnace would shut off on high limit if it was overheating because the blower was working incorrectly.
  • May 28, 2008, 06:35 PM
    Alfred Ament
    Thanks for that info!

    Alas ,I noticed burner takes to ignite for aprox. 5 minutes too,after thermostat is set for heat !
    I have the gas company check for full supply of gas tomorrow, and then what!
  • May 29, 2008, 02:10 AM
    hvac1000
    Clean flame sensor