  • May 27, 2008, 12:46 PM
    jiaoniang99
    Blower will only work in Heat, not Fan-On or Cool-Auto
    Hi, I have a York system about 10 years. Its control board keep giving me problem. Most last year was the connection problem of the socket where the t-stat's 4 wires go in. I finally soldered a fly-wire for the W for heating issue last winter to fix it.

    Now, the summer comes and the cooling is not working. I doubled checked by shorting the R-W, the heat went on and the blower went on, everything is fine. By shorting R to G or R to Y, there was some flowing fluid noise inside the furnace, the external compressor went on and cool, but the blower will not work.

    The R-G connection doesn't turn on the blower, yet it seems to turn on the compressor, or at least some fluid is running through the furnace.

    How can I be certain it is the blower or the board has problem? The blower had replaced a cap last year when R-G didn't do anything including the fluid noise, yet R-W nor R-Y can make the blower run.

    Thanks!
  • May 27, 2008, 04:20 PM
    hvac1000
    A/C blower relay on board is probably defective.
  • May 28, 2008, 07:48 AM
    jiaoniang99
    Thanks for your quick reply. If so, is changing the relay a feasible solution or the whole board?
  • May 28, 2008, 08:07 AM
    hvac1000
    Whole board. The relay might be impossible to find then you are still going to have to plat with a printed circuit board. Not a good thing. Get the board.