  • May 25, 2008, 05:42 PM
    reachief
    Under cabinet lighting
    I am installing separate xenon lights of various lengths, typically 13", in 7 locations, each with its own transformer.
    1st: Can these all be on one 15 amp circuit?
    2nd: Wiring? I assume that I provide power to the switch and then daisy chain 14/2 wire to each fixture (daisy chain: one wire in and one wire out of each fixture).
    Russ
  • May 26, 2008, 06:20 AM
    df244
    It is possible to put all the lights on one circuit but not knowing the wattage of the xenon light strips it is difficult. Here is the calculation to verify that the existing circuit is large enough.

    total wattage (include any other appliances, lamps... connected to this circuit) divided by the voltage = total amps

    A 20 amp circuit should not be loaded more than 16 amps.
    A 15 amp circuit should not be loaded more than 12 amps.

    Hope this helps.