  • May 23, 2008, 01:16 PM
    wek
    Power for house
    How do you figure out how much power is needed for the whole house?
  • May 23, 2008, 04:09 PM
    mr500
    Power as in voltage, amps ? What project are you working on?
  • May 23, 2008, 04:38 PM
    Washington1
    By doing a demand load calculation.

    This doesn't mean you are going to add up all the circuit breakers, or all the loads--seeing that not all loads will be utilized simultaneously. So, there is a number of factors (demand factors) that has to be considered. Where do we start: The NEC-Article 220.

    First: General lighting load
    Second: AC over Heat or versus heat
    Third: App's (Appliances)
    Fourth: Dryer
    Fifth: Cooking appliance or equipment
    Sixth: Service or feeder size