Ask Me Help Desk

Ask Me Help Desk (https://www.askmehelpdesk.com/forum.php)
-   Electrical & Lighting (https://www.askmehelpdesk.com/forumdisplay.php?f=105)
-   -   Dishwasher wiring issue (https://www.askmehelpdesk.com/showthread.php?t=219054)

  • May 23, 2008, 09:59 AM
    Bobo9812
    Dishwasher wiring issue
    :confused: I'm installing a new dishwasher. It is on a 20amp breaker. The wire from the dishwasher won'r reach the junction box. The dishwasher is wired for a 120V for a 15 amp circuit.
    Can I SAFELY use about 8 feet of 12 gauge wire to run from the junction box to the dishwasher?

    Thanks
  • May 23, 2008, 10:51 AM
    KISS
    I'm confused too so assumptions:

    1) a 20 A, 12 AWG circuit is 8' too short
    2) Dishwasher requires a 120 V 15 A circuit

    Going with these assumptions:
    You have to make the splice in an accessible junction box UNLESS a special splice connectior is used and approved by your AHJ. This one: TYCO ELECTRONICS (ALR) CPGI-1116415-2 NON-METALLIC ROMEX CABLE TAP AND SPLICE CONNECTOR. The key is accessible.

    I'd extend with 12 AWG.

    I'd change the breaker from 20 to 15 amps. That will make everybody happy.
  • May 23, 2008, 04:44 PM
    Washington1
    Keep, you are given away-- waaaay too many secrets (Joke) :)