  • May 18, 2008, 10:26 AM
    nikki99cat
    Furnace repair
    What would cause the round plastic sight hole to the furnace burners to melt around the edges.
  • May 18, 2008, 10:30 AM
    hvac1000
    Probably overheat.
    If not melted through just a bit of heat mark on the edges it could be normal with age.

    BUT it could also indicate improper combustion air control or needs a professional adjustment.
  • May 19, 2008, 07:34 AM
    wmproop
    2 much heat
  • May 19, 2008, 07:55 AM
    therinnaiguy
    Blocked flue vent, not enough combustion air, bad safety sensor, improper gas/air mixture, all of the above. Get a technician to inspect it.
  • May 19, 2008, 07:59 AM
    KISS
    A natural gas furnace (NAT) operating on propane (LP) without the proper orfice conversion.