    Remodeling kitchen. I now have an oven with 8AWG and a 30 amp breaker. The new oven requires 40 amps. The run is 20 feet. Will the 8 awg do with a 40 amp breaker?

    Thanks,

    Shortround3.
  • May 18, 2008, 08:22 AM
    donf
    8 AWG - Copper, is rated for 40 Amps.
  • May 18, 2008, 08:51 AM
    stanfortyman
    #8 in NM and UF cable is rated for 40 amps.

    #8CU THHN and most other conductor/cable types is rated for 50 amps.
  • May 18, 2008, 01:48 PM
    Washington1
    Quote:

    Originally Posted by stanfortyman
    #8 in NM and UF cable is rated for 40 amps.

    #8CU THHN and most other conductor/cable types is rated for 50 amps.

    Good answer! Complete, with facts!