House has a 120 volt, q-mark hyd electric baseboard heater ran on 14/2 cable with 2 recepticales of the same feed. 15 amp breaker in panel.
Is the OK?
Thx
![]() |
House has a 120 volt, q-mark hyd electric baseboard heater ran on 14/2 cable with 2 recepticales of the same feed. 15 amp breaker in panel.
Is the OK?
Thx
What is the amperage listed on the heater.
If you are using the baseboard heat, you will only have 4.4 amps available.
I would recommend putting the heater on an independent 15 amp circuit
That unit requires a dedicated 15A circuit.
A 20A circuit could be shared with a few other items, but shouldn't really.