  • May 12, 2008, 11:21 AM
    yurka80
    Replacement of Carrier Heat Pump Thermostat with Honeywell TH6000 series thermostat.
    I have a Carrier Series 50QT Electric heat pump that still uses the original non programmable thermostat. I am trying to replace it with Honeywell TH6000 series programmable thermostat.

    The wiring on the existing Thermostat as follows:

    O - White, I am thinking this is the Reversing Valve?
    Y - Blue, Cooling stage 1?
    R- Red, Power
    E - Jumpered to W2 Emergency Heat relay?
    G- Fan
    C - 24 Vac Common?

    What is the proper mapping of the connections to the new thermostat? And also what are the right programming options for it?

    :confused:


    Thanks!
    Yuriy
  • May 12, 2008, 11:57 AM
    hvac1000
    First of all you did not supply the complete model number. There is a letter after the 6000 part.

    Here is a wiring diagram that will cover them all.
    Just follow the directions

    http://customer.honeywell.com/techli.../69-1920ES.pdf

    If you cannot follow the directions then you will probably have to call for a pro to do the install. Way to many variables to and to many chances of damaging the unit.

    NOTE Honeywell has a toll free number to call if you need them.
  • May 12, 2008, 12:13 PM
    yurka80
    I used that guide, namely the wiring schema for 2H/1C Heat Pump System, the problem is that it's calling for 7 wires, one for L, but my existing Thermostat only has 6. Also when I did wire it, once my heat turns on, it immediately turned on the Emergency Heat, but the air coming out of the registers was still cold.
  • Oct 11, 2009, 01:39 PM
    enirpmet
    I have they same problem with the emergency hgeat turning on immediately. What was your resolution?

    Thanks

    Matt
  • Apr 27, 2011, 03:00 PM
    Seann
    hi

    first of all this is a professional thermostat and should be installed only by a contractor,however
    O-O/B
    Y-Y
    G-G
    E-E
    C-C
    R-R^Rc
    as per wiring it seems to be Heatpump all electric
    hense the ISU also has to be changed so speak to a contractor or check installation guide