Recently purchased new mobile home with a 200 amp breaker inside.the distance between the outside pole and inside breaker is about 70 feet.what size,or type,or gauge wire do i need to run.
Lost in paradis... :) :confused:
![]() |
Recently purchased new mobile home with a 200 amp breaker inside.the distance between the outside pole and inside breaker is about 70 feet.what size,or type,or gauge wire do i need to run.
Lost in paradis... :) :confused:
There is a type of cable for moblie homes, aluminum underground service feeders , see the attachment.
Typical 200 amp feeder for 70 feet will be the #4/0-#4/0-#2/0-#4 cable.
It is rated for direct bury, but you may consider installing a 3" PVC conduit to sleeve and protect the cable most of the distance.
Be sure to read the manufacturers instructions for terminations, usually need to be wire brushed and have anti-oxidant compound applied. Incorrect connections are the only reasons al wire is noted for.
Thanks Again Tk.