    GEORGE HUBBARD
    Wire Size For 200 Amp Service
    Recently purchased new mobile home with a 200 amp breaker inside.the distance between the outside pole and inside breaker is about 70 feet.what size,or type,or gauge wire do i need to run.
    Lost in paradis... :) :confused:
  • Feb 23, 2006, 02:31 PM
    tkrussell
    There is a type of cable for moblie homes, aluminum underground service feeders , see the attachment.

    Typical 200 amp feeder for 70 feet will be the #4/0-#4/0-#2/0-#4 cable.

    It is rated for direct bury, but you may consider installing a 3" PVC conduit to sleeve and protect the cable most of the distance.

    Be sure to read the manufacturers instructions for terminations, usually need to be wire brushed and have anti-oxidant compound applied. Incorrect connections are the only reasons al wire is noted for.
  • Feb 23, 2006, 02:45 PM
    GEORGE HUBBARD
    Thanks Again Tk.