    charles1962
    No volatage to outlets and lights
    I was trying to find a breaker to a circuit and took the switch wires and touch them together it cause the lights to go off,but the breaker did not trip and now I can't get the lights back on also the main breaker was arcing as I turn it on and off
  • Apr 14, 2008, 03:49 PM
    ballengerb1
    Are you sure that the wires are not still in contact with each other or part of the box? It sounds like you still have a dead short. Did you mean to say main breaker is arcing or just the breaker for the line you were working on?
  • Apr 14, 2008, 05:08 PM
    stanfortyman
    Quote:

    Originally Posted by charles1962
    but the breaker did not trip and now i can't get the lights back on also the main breaker was arcing as i turn it on and off

    CALL AN ELECTRICIAN right away!
    This just became a pro-only situation. Replacing a main breaker is NOT a DIY job.
    It is actually likely that the panel will need to be replaced since the buss is likely burned.
  • Apr 14, 2008, 05:11 PM
    stanfortyman
    BTW - who told you it was OK to short out wires to find a breaker?? We don't do this any more.
    If you want to continue in this trade and look like a pro I'd lose that practice right away!