New A/C Condenser - What wire gauge for supply?
Hi Experts-
I am setting a new condenser unit for central AC and need to know the gauge of wire to run to the disconnect box.
From the Manufacturer of the condenser:
13 SEER unit (higher efficiency)
Minimum Ampacity: 14.5
25 Amp Breaker
LRA 68
According to the need for the 25 amp breaker, NEC indicates that it must be #10 AWG wire, as 12 must not be run for any circuit over 20 amps.
However, the line length will be reasonably long- approximately 70 feet from the panel box to the disconnect at the unit. (Has to run clear across the house & garage.) I want to be sure that 10 AWG will be heavy enough to cope with the increased cable length.
Thanks in advance for any insights!