-   -   Maximum load allowed on a branch circuit used for fixed resistance heating? (https://www.askmehelpdesk.com/showthread.php?t=201963)

  • Apr 3, 2008, 10:52 AM
    gregpyke
    Maximum load allowed on a branch circuit used for fixed resistance heating?
    What is the maximum load allowed (%) on a branch circuit used solely for fixed resistance heating?
  • Apr 3, 2008, 01:06 PM
    stanfortyman
    Fixed electric heat is always considered a continuous load, so it must be figured at 125% of the load. In terms of the branch circuit you can load it to 80%.