  • Apr 1, 2008, 05:29 PM
    plumeria
    Weil-McLain Boiler settings? Look right?
    Weil-McLain Gold Oil
    Model: WTGO-4
    Series: 3
    Net Output... Water 128 MBH
    Pressure set at 22
    Water Temp at 162
    Feet H20 at 40


    Water Heater is Amtrol Boilermate WH7ZDW
    41 gallon
    Work Pressure 150 psi
    Test Pressure 300 psi
  • Apr 1, 2008, 08:08 PM
    hvac1000
    Pressure is usually 12 instead of 22 on a single story house.
  • Apr 1, 2008, 11:11 PM
    plumeria
    The house is three story, with three zones (two small apartments), and the house has the main level, and bedrooms upstairs. I have had problems with registers working since the installation The upstairs bedrooms weren't getting heat. The company keeps turning up the pressure, I think that is what I believe they keep doing to try and solve the problem. I am wondering if something isn't hooked up correctly. The installer is baffled at why the heat isn't working in all the registers. It was professionally installed, and it's a small island in Alaska with basically one company on our island. They will work upstairs, but not downstairs, and visa versa. The apartments are getting heat, but said they can hear bubbling in the radiators. They were all bleed on the installation from my understanding. Any suggestions
  • Apr 2, 2008, 01:33 AM
    hvac1000
    Now we have more of the story to work with.

    Have them install automatic bleeders at the highest point in the system.
    Just because it was bleed at start up when new does not mean no more air got in the line.

    See Maid O mist here

    KingSolar.com: No. 67 Auto-Vent - 1/8inch I.P. male connect, Up to 50psi


    Use this adapter and 1/4 inch copper tube for attic or any install when safet water venting is absolutely needed. If the vent gets plugged up and wants to leak this little item prevents that from happening by running any overflow from the valve to the outside of the house. I have them but they never have had to be used in over 30 years. I just consider it insurance fror leaks.

    KingSolar.com: No. 7A Connector - Connector for use with Maid-o-Mist Auto-Vents

    Also spirovent is a great company and makes very good air elimination products.

    Spirotherm, Inc. - World Leader in Air Elimination and Dirt Separation Technology


    Good luck with your system.