  • Mar 21, 2008, 05:13 PM
    el hefe
    No auto fan in heat mode
    Have a carrier outdoor package unit A/C and electric heat. Recently changed from the carrier programmable to a standard heat/cool stat. original stat had a light that would indicate when the filter needed changed, assume this was the blue wire that we did not connect when installing the new standard stat. r-red, w-heat, g-green fan, y- cool and capped the blue. Unit heats but will not blow in auto mode, fan runs in on mode and also runs properly in auto when in cooling mode... entire system operated correctly prior to changing t stat... any help on what's wrong?
  • Mar 21, 2008, 05:26 PM
    hvac1000
    There is a fan control switch located in the outside unit. It could be a thermo disc or a time delay. When the unit heats up outside this part tells the unit to turn on the blower. Post model of thermostat and the brand name and I will check on the thermostat possibilities.
  • Mar 21, 2008, 06:13 PM
    el hefe
    Thank you. We are trying to install a Honeywell CT31 non programmable... the carrier unit outside is a model 50ZP-036---311 with a serial of 1799G42426
  • Mar 21, 2008, 06:17 PM
    el hefe
    We have let the unit run in heat mode for up to 3 minutes with no fan response in auto mode, in on mode it blows HOT air... the t-stat instructions stat that if used with an electric furnace set the adj. lever to .3 but of course this made no difference, the fan sill will not operate... we are presently re-installing the original Carrier programmable to see if the unit will still operate properly with the original stat
  • Mar 21, 2008, 06:20 PM
    el hefe
    This unit is probably 30 yrs old on a dbl wide in Florida that my father is working on, I'm in Maryland trying to assist him over the phone... Thanks for your help
  • Mar 21, 2008, 06:43 PM
    el hefe
    With the original Carrier t-stat now re-installed the unit operates properly in heat and A/C mode... evidently our Honeywell is incompatible... suggestions?
  • Mar 21, 2008, 08:39 PM
    hvac1000
    From what I read here

    http://customer.honeywell.com/techli.../69-1809EF.pdf

    You might have the wrong stat.
  • Mar 22, 2008, 05:04 AM
    el hefe
    Any suggestion on what make/model t-stat will work/ Thanks!
  • Mar 22, 2008, 05:48 AM
    hvac1000
    You need one that will work with electric heat.