  • Mar 11, 2008, 11:35 AM
    carpetman
    Blower working,hot surface ignitor not lighting up
    My furnace is a Carrier,about 9 years old. My blower runs but there is no heat. Have done some research so I replaced the HSI because there was a white spot on it and it was not lighting up. It still is not lighting up. Could someone tell me what I should do next. Thanks.
  • Mar 11, 2008, 01:58 PM
    hvac1000
    Check for voltafge at the HSI. Then check for voltage at the board plug in.

    If the board has a fuse check it also.
    Have you replaced the thermostat lately?
  • Mar 11, 2008, 03:18 PM
    carpetman
    Have not checked voltage. Is it supposed to be at 120v? Have not replaced thermostat but recently changed batteries. Checked fuse it was a 3 fuse OK. Where do I check the voltage on the board?
  • Mar 11, 2008, 03:23 PM
    hvac1000
    Follow the leeds bach to the board or unplug the HSI and test there. Set volt meter at 120.

    How many blinks does your circuit board show for a fault code. Fault codes will be listed on the inside of the blower compartment door.
  • Mar 11, 2008, 04:06 PM
    carpetman
    The led light is blinking a 3-3. Went and purchased a digital voltage meter. You can set it for AC at 200 or 500. I set it at 200, put the two probes where the HSI connects and it read a 0. Not sure if Im doing it right, sorry first home trying to teach myself.
  • Mar 11, 2008, 05:26 PM
    hvac1000
    HSI is 115 volt amp draw 1.0

    33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open.

    There is a wiring diagram inside the blower. It should also contain a blink code number list and fault.
  • Mar 11, 2008, 05:31 PM
    hvac1000
    ? Is the blower motor you are talking about the main house blower or the draft inducer motor on the front of the unit?
  • Mar 11, 2008, 06:31 PM
    carpetman
    It's the main blower at the bottom of the unit. Its big. It is a #33 , flame rollout is open, but it also states if open for more than 3 minutes it's a #13 lockout.? What does this mean, next step? Thanks.
  • Mar 11, 2008, 06:45 PM
    hvac1000
    13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
    Open longer than 3 minutes.
    - Control will auto reset after three hours. - Refer to #33.


    33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
    Run for 4 minutes or until open switch remakes whichever is longer. If open
    Longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
    Status code #33 continues to flash until blower shuts off. Flame rollout switch
    Requires manual reset. Check for: - Restricted vent
    - Proper vent sizing - Loose blower wheel - Excessive wind
    - Dirty filter or restricted duct system.
    - Defective blower motor or capacitor. - Defective switch or connections.
    - Inadequate combustion air supply (Flame Roll-out Switch open)
  • Mar 11, 2008, 08:14 PM
    carpetman
    How do I know if I have any defective switches or connections? Vent sizing OK, blower wheel OK, filter OK. Do I need to manually reset flame rollout switch, if so where is it and how? Also why is there no voltage when I test the plug that connects to th HSI?
  • Mar 11, 2008, 10:02 PM
    hvac1000
    Flame roll out switch located near front of furnace right above burner area.
  • Mar 12, 2008, 01:28 PM
    carpetman
    What is the little black wheel in front that says rotation on it?
  • Mar 12, 2008, 01:33 PM
    hvac1000
    That is the combustion/vent fan. It needs to be running for the unit to fire up.
  • Mar 12, 2008, 01:41 PM
    carpetman
    So do you think I should replace it? Does that explain having no voltage on the HSI as well?
  • Mar 12, 2008, 03:22 PM
    hvac1000
    What is the little black wheel doing? Does it run/spin?

    You need to test the motor on the fan for the little blower wheel before you replace it.
  • Mar 12, 2008, 03:40 PM
    carpetman
    Its not spinning at all. And how do I test the motor on the fan.
  • Mar 12, 2008, 04:48 PM
    hvac1000
    Remove connector. Apply rated voltage to wires. Motor should be 120 bolts.
  • Mar 12, 2008, 05:09 PM
    carpetman
    I applied my meter to the wires that plugged into the fan and it read 0.
  • Mar 12, 2008, 05:16 PM
    hvac1000
    Yiu are not getting voltage at the board. If you want to test the fan you need to apply 120 volts to the fan motor from another source.
  • Mar 12, 2008, 05:18 PM
    hvac1000
    Post the exact model number of your unit.