  • Mar 9, 2008, 11:57 AM
    edfinley
    Electric Dryer Hookup
    I need to replace an electric dryer. The old dryer is hard wired. What is the code for hooking up the new dryer?
  • Mar 9, 2008, 03:03 PM
    stanfortyman
    You need a form of disconnect. For a dryer, 99.99999% of the time this is a cord and plug.

    How old is this circuit?
  • Mar 9, 2008, 03:18 PM
    Stratmando
    You can Install 3 or 4 wire Dryer cord. New Construction and remodel require 4 wire.
    Yours may not apply or have extra wire. Connect 3 wire setup or pull 4th wire (#10) for the 4 wire setup;
    Remember you have to remove the strap where cord connects to dryer so Neutral and Ground are separate.
  • Aug 7, 2008, 03:14 PM
    benaround
    Quote:

    Originally Posted by edfinley
    I need to replace an electric dryer. The old dryer is hard wired. What is the code for hooking up the new dryer?

    ED, Does the circuit come from a main panel or a sub-panel ? This will make a difference

    If 3wire cord or 4 wire cord is needed.
  • Aug 7, 2008, 03:25 PM
    stanfortyman
    Frank, you do realize this thread is from 5 months ago?
  • Aug 7, 2008, 03:55 PM
    tkrussell
    Besides, Stan, this is wrong anyways:

    Quote:

    Originally Posted by benaround
    ED, Does the circuit come from a main panel or a sub-panel ? This will make a difference

    if 3wire cord or 4 wire cord is needed.

    Whether the panel is the main or a sub does not affect the branch circuit, which must be a 4 wire.
  • Aug 7, 2008, 04:06 PM
    Washington1
    I was wondering where in the heck this came from:
    Quote:

    ED, Does the circuit come from a main panel or a sub-panel ? This will make a difference

    If 3wire cord or 4 wire cord is needed
  • Aug 8, 2008, 01:31 PM
    benaround
    Quote:

    Originally Posted by tkrussell
    Besides, Stan, this is wrong anyways:



    Whether the panel is the main or a sub does not affect the branch circuit, which must be a 4 wire.

    Maybe you should look at 250.140 ex.3 NEC2005 , this is an existing circuit.

    Still think I'm wrong?
  • Aug 8, 2008, 02:13 PM
    tkrussell
    Yes,


    Quote:

    Originally Posted by benaround
    ED, Does the circuit come from a main panel or a sub-panel ? This will make a difference if 3wire cord or 4 wire cord is needed.

    This is still wrong, as per Section 250.24(5), which refers to your reference by the words "except as otherwise permitted in the article."

    This statement made does not refer to the existing branch circuit, that you now mention.

    I have read Section 250.140 ex.3 several times,even have referred to it here in the forum to help those with existing circuits with relief from replacing or upgrading that circuit.

    Since Sec 250.24 is ahead of Sec 250.140, it supersedes and take precedence, and does not affect whether a main panel or a subpanel dictates if the circuit is to be 3 or 4 wire. That fact is only determined if the range or dryer Branch Circuit is existing.

    Two entirely different statements. Your first is wrong, the second is correct.
    Perhaps that is what you meant in the first post?
  • Aug 8, 2008, 02:14 PM
    stanfortyman
    I will say, ben is right about the panel. This is one of the reason I asked how old the circuit is.

    An older existing circuit could be 3 or 4 wire depending on conditions. This is what Strat was getting at.
    If the cable were proper for it, a 4-wire receptacle and cord would be the best bet.


    I really hate it when folks post a question and then disappear. We could speculate all day about this, but the fact is the OP is MIA and we need more info.
    I personally think it is quite selfish that folks do this. We take time from our personal lives to help folks for free and some people feel it is no big deal to waste that time. :mad:
  • Aug 8, 2008, 02:21 PM
    stanfortyman
    I do also see TK's point. The panel is not the only deciding factor, it is one of them. That's why I said that just above.

    I think there is just some misunderstanding going on, that's all.
  • Aug 8, 2008, 02:27 PM
    tkrussell
    How does a panel classification cause a branch circuit to be 3 or 4 wire?

    Whether a branch circuit is 3 or 4 wire is not determined by the "type" of panel.

    Keep in mind, there is no official, technical term "subpanel" as defined by the NEC.

    I just don't see or understand the misunderstanding.

    This is still an incorrect statement:

    Quote:

    Originally Posted by benaround
    ED, Does the circuit come from a main panel or a sub-panel ? This will make a difference if 3wire cord or 4 wire cord is needed.

  • Aug 8, 2008, 02:41 PM
    Washington1
    Quote:

    Originally Posted by tkrussell
    How does a panel classification cause a branch circuit to be 3 or 4 wire?

    Whether a branch circuit is 3 or 4 wire is not determined by the "type" of panel.

    Keep in mind, there is no official, technical term "subpanel" as defined by the NEC.

    I just don't see or understand the misunderstanding.

    This is still an incorrect statement:

    I agree!




    Quote:

    I really hate it when folks post a question and then disappear. We could speculate all day about this, but the fact is the OP is MIA and we need more info.
    I personally think it is quite selfish that folks do this. We take time from our personal lives to help folks for free and some people feel it is no big deal to waste that time.
    I agree above agree!! I've said the same thing on other sites.
  • Aug 8, 2008, 02:59 PM
    benaround
    Quote:

    Originally Posted by tkrussell
    How does a panel classification cause a branch circuit to be 3 or 4 wire?

    Whether a branch circuit is 3 or 4 wire is not determined by the "type" of panel.

    Keep in mind, there is no official, technical term "subpanel" as defined by the NEC.

    I just don't see or understand the misunderstanding.

    This is still an incorrect statement:

    OK, one more time. 250.140 ex3 is what we are talking about, it says in it's last words,

    " ---and the branch circuit ORIGINATES at the SERVICE EQUIPMENT".

    That's how a panel classification causes a branch circuit to be 3 or 4 wire.

    Am I still wrong ?
  • Aug 8, 2008, 03:04 PM
    tkrussell
    Yes.
  • Aug 8, 2008, 03:10 PM
    benaround
    Quote:

    Originally Posted by tkrussell
    Yes.

    LOL!!
  • Aug 8, 2008, 03:20 PM
    tkrussell
    Well seems you got a kick out of my answer.

    Since you seem so intent on confusing the issue, simply by the word "originating" please explain a couple of scenarios where each "type" of panel determines whether the circuit is 3 or 4 wire.

    Perhaps if you think it through you will discover that your first post

    Quote:

    Does the circuit come from a main panel or a sub-panel ? This will make a difference if 3wire cord or 4 wire cord is needed.
    Is simply wrong.

    Please cite any applicable code section, and not 250.140, as it is only relevant to the "existing" branch circuit, no matter what "type" of panel it originates from.
  • Aug 8, 2008, 03:29 PM
    Washington1
    benaround,

    I like that you are person who seeks clarity (great trait)! Yet, re-read what you wrote. Does it make sense? If so, clarify.
  • Aug 8, 2008, 03:36 PM
    benaround
    tkrussell,

    The OP stated he had a hard wired dryer circuit (existing) and now he has a new dryer.

    If it's a 4 wire circuit, this is all for nothing.

    If it's a 3 wire circuit and does not originate in the service equipment (main panel) then

    The circuit will have to be replaced with a 4 wire circuit.

    That's what the code book says plane and simple, if you can't follow this, or you don't do

    It this way, that's fine, but before you call a person wrong make sure they are.
  • Aug 8, 2008, 03:46 PM
    Stratmando
    Bottom line, New construction and remodel require 4 wire, doesn't matter what panel.
    Since this is replacement, 3 wire is fine, IMO. I would also have a cord and receptacle.