-   -   Bryant Evolution (carrier infinity) Control and Honeywell Fresh Air Vent. (https://www.askmehelpdesk.com/showthread.php?t=19242)

  • Jan 30, 2006, 07:09 PM
    mooredan
    Bryant Evolution (carrier infinity) Control and Honeywell Fresh Air Vent.
    I have an Bryant Evolution system installed. This is the same as a
    Carrier Infinity system. This consists of a 355MAV furnace, a 598B a/c
    And SYSTXBBUID01 Evolution control.


    Also installed in this system is a Honeywell Y8150 ventilator and a
    Honeywell HE440 steam humidifier.


    The evolution control is a recent addition to the system replacing a
    Honeywell 8320 thermostat.


    Previously, either the humidifier or ventilator could turn on the
    Furnace fan. (by applying 24VAC to the G terminal of the furnace's
    Control board).


    After installing the control, which uses the furnace's data port on the
    Control board, a call to turn on the fan by either of these components
    Is ignored. However, the furnace and a/c operates normally with the
    Evolution control.


    Does anyone know what's going on here? Does hooking up the control
    "lock out" the traditional thermostat connection controls? How can I
    Get the ventilator or humidifier to turn on the fan in this
    Configuration?

    Thanks

    Dan


    Followup:

    I have confirmed that when either the humidifier or ventilator wants
    The fan to come on, they do put 24VAC on the "G" terminal. However, the
    Fan does not come on.


    If you're familiar with this system, you'll know that the control does
    Not connect to the traditional furnace terminals G/W/Y/... but connects
    To the furnace's data port (4-wire) on the system board.


    It seems that the presence of a control (versus a traditional
    Thermostat) is locking out (ignoring) the G terminal.


    My question is does anyone have any experience with this system with
    This type of configuration and if so, how can I get the an auxiliary
    Piece of equipment to successfully make a fan call?


    Dan
  • Jan 30, 2006, 09:05 PM
    labman
    Rather than waiting for an answer here, you may be better off with Bryant's or Honeywell'stech service or web site.
  • May 5, 2008, 02:46 PM
    The79Bomb
    The Humidifier is connected to port c and port "hum" on the control board in the furnace. I believe the thermostat is supposed to control the Humidifier using it's own humidistat not the other way around. It may be that the thermostat believes there is no Humidifier present. When you first configure the thermostat it asks for the presence of a fresh air unit and Humidifier and you have to set these to yes or no. check the thermostat manual and make sure these are set to yes.
    Yours, Tim