I am working on a 52 stoey building.. I want to know what is the static load of chilled water working pipe in riser if building height is 200 mtr. pipe size is 200mm and riser is going across the building..
![]() |
I am working on a 52 stoey building.. I want to know what is the static load of chilled water working pipe in riser if building height is 200 mtr. pipe size is 200mm and riser is going across the building..
The Static Laod will Be Around 20 Bar . Where 1 Bar for almost 3 floors which is Around 3.1 m , coming to a 10 m per 3 floors .
I am working also in a 51 Level Building , and my Risers are working just Fine!!