    I am installing a steam generator for a steam shower. The unit draws 38 amps. I need a GFCI breaker. The run is 35 feet. What size wire and breaker do I need?
  • Mar 2, 2008, 01:55 PM
    Stratmando
    2 #6's for hots, #10 for ground, and a #8 for Neutral. 50 Amp GFI breaker. 3/4" Conduit.
  • Mar 2, 2008, 02:53 PM
    stanfortyman
    Quote:

    Originally Posted by JKc
    I am installing a steam generator for a steam shower. The unit draws 38 amps. I need a GFCI breaker. The run is 35 feet. What size wire and breaker do I need?

    Is this 240V or 120/240V?
    Most steam gennys I have wired were straight 240v thus requiring X/2NM cable w/ground.
    In your case 6/2NM would be correct. Unless you run conduit the WHOLE way, then you can use two #8THHN with a #10 ground.