T&P Valve discharge line leaking water
I have a 3 year old gas water heater with an expansion tank. The water temp is set to 120 degrees. For the last couple weeks, the discharge line has been leaking water out of the overflow pipe. I've been told that simply replacing my T&P valve will not solve this problem. I had my water heater inspected and the person said the water pressure regulator (Pressure Reducing Valve on main line) is not controlling the flow into the system when static. With no water flowing the pressure tested at the tank valve (Water Heater drain faucet) was 140 PSI. When you start a faucet running in the house the pressure dropped to 60 PSI. Then, with the water turned off, it very slowly started creeping back up and after 10 minutes and was at 75 PSI and rising. So, I would appreciate anyone's feedback as I'm finding it hard to believe that I have to pay to have my PRV replaced on a 3 year old house. Also, the Expansion Tank was tested as is working correctly. Thanks