AC Power Issue with Honeywell RTH7400 Thermostat
I've installed a Honeywell RTH7400 thermostat on a heat pump system with electric resistance auxiliary heat. The thermostat is properly wired and programmed but would not operate properly. It would run the heat pump for less than a minute and shut the system down.
After an hour with Honeywell's India call center we found the following. Pulling the 'C' wire from the thermostat base permits the system to run normally. In other words, the thermostat runs fine on internal 'AA' battery backup but not AC power.
The tech says the thermostat is rated for 24-30VAC at 1A and questioned power quality which is not an issue. I ran a wire pair to the baseplate and measure 28.3 volts which sags to 26.5 with relay closures.
For some reason this thermostat does not like to see AC power... which the old dual mercury switch model never minded.