Originally Posted by stanfortyman
				
			
			First off, where are the breakers for the items not working right? In the sub panel I assume.
What brand is the main panel? If it is GE or FPE there is a real chance you installed the sub-feed breaker incorrectly. With those panels you can easily install the 2-pole breaker with both stabs on the same leg of the service. This will give you only 120v to the whole sub-panel instead of the required 120/240v.
Second, did you get this tub inspected? I hope so but I assume not.
If you ran 6/3 cable to the tub outside the house this is very illegal. You MUST run conductors in conduit using an insulated ground for the outside portion of the wiring to a spa or hot tub.
Are you aware of the other important codes related to wiring a spa or hot tub? This is NO place you want to mess around if you are not sure of what you are doing.