    Wire to a 100A sub-panel
    I want to run copper wire from my 200Amp main electrical panel to a 100Amp sub-panel. The 100Amp panel will feed a heat pump compressor, air handler with heat strips (total load = 70 amps) and about 4 20 amp outlet lines. I have previously wired a 60 Amp sub-panel in this house.
    The panels would require about 12 feet of wire from one to the other.
    What size wire should I use for the 100Amp panel?
  • Feb 15, 2008, 07:30 AM
    tkrussell
    #4 copper is the min size allowed for a residential 100 amp feeder.