    I have a generator that puts out 5500watts & has (4) 120 volt 20 amp receptacles and 1 Nema L14-30 120/240volt receptacle. I am running a new wire to the panel so I can hook my travel trailer up. The RV requires a 30 amp 120volt receptacle. I have already purchased the wire and connectors but wanted some advice on where to hook the wires into the back of L14-30 receptacle . I need to have 1 ground, neutral,and hot lead but I need to be certain that I still have enough voltage and amperage to run the camper.
  • Feb 13, 2008, 08:01 PM
    KISS
    First, I want you to look here:

    Look at the watertight connectors. The trailer should have pins.

    The connector should have terminals X, Y, G (Green terminal) and a white terminal.

    G is ground. White is neutral. Pick X or Y for the 120 V.

    5500/240 is about 23 Amps and I'll bet the generator is fused for 20. Generally the ratings are at the higher voltage.

    If it needs 30, you'll be a little short.
  • Feb 13, 2008, 08:02 PM
    Washington1
    Why would you supply power to your generators 30A receptacle to supply power to your RV?

    Take the generator out of the picture.

    You need to go buy yourself a nema 3R box with 30a 125v RV receptacle, and a 30A RV extension cord with RV plugs.
    Run a #10 copper wire from panel to 30A NEMA 3r RV box, then plug your RV cord into the outlets.