We have a group home with a 8+ year old Lochinvar 300,000 BTU LP gas outdoor furnace. I suspect that the installer just shot from the hip on size (retrofit for ceiling electric). It is supplying 4 zones 60 to 100 feet away in the attic with 18"x24" heat exchangers (if memory serves). These are in the AC plenums. We just had all the zone piping upsized to the correct diameter (1 inch HePEX, you don't want to know what was there). It is using Taco 007's for the zones and a 009 for the furnace loop into the garage where the header is.
I happened to check it today because the weather is cold, 5 to 15 degree outdoor temps and a good wind, and this is the first time I got to see it since refitting. All 4 zones were calling for heat, and the furnace would fire for approx 2 minutes and then shut off for 2 minutes. This says OVERSIZE to me, and it will only be worse with less demand. Is there anything to do to improve things? I also noticed that right before it would shut off at the upper temp limit the pressure gauge would fluctuate +10 to 15 lbs and I would hear a banging or bumping in the pipes. What gives?