Need simple load shedding.
I've discovered that I can't increase our 200 amp service for a reasonable price. The 400 amp panel and installing it is easy and low cost (relatively), but changing the breaker on the pole and the 200 feet of underground wire that is not adequate for 400 amp is not. We're in a rural area and the electric co-op requires the breaker under the meter at the service entrance.
The reason for increase the service is to use a large welder, stamping press, and demand heater in a shop area, but not simultaneously.
I know it's possible, but I can't find the contactor or relays I need to do this.
I'd like to have the energizing of the large 19.2 KW load cut a 10 KW and/or an 8KW load. The 19.2 load is the demand heater connected to two 40 amp breakers (it has two separate circuits), 10 KW load is on one 40 amp, and the 8K load on a 30 AMP breaker.
If there's an easy mechanical way to do this, my problem would be solved.
Essentially, the 10 KW load and the 8 KW load (for a large well pump at 900 feet or so) are interruptible at any time as neither has any safety or convenience issues if they are off for the 90 minutes or so per day, but not continuous, that I actually need the 19.2 KW for heavy shop work.
I'm thinking that a normally on contactor in the 10 KW 40 amp and 8 KW 30 amp circuit that would go OFF when the 19.2 KW load (either of the two circuits) is energized.
All load control items that I can find seem to be hugely expensive and for use only by the power company.
Thanks!