  • Feb 3, 2008, 12:25 PM
    davidjs
    Goodman AE 24-08 Blower/control issues?
    Hi,
    I have a Goodman AE 24-08 interior blower unit for my heat pump.

    Recently the blower stopped turning on, while the outside unit would run. Checking in the panel, the motor was trying to kick over, but couldn't get started. If I turned the blower by hand, (to get it started), it would run fine.

    I actually ended up upping the speed, and it starts now, but I'd like to actually fix the problem, since I feel like I'm living on borrowed time (sometimes the blower motor sounds slightly uneven, like it's building up then decreasing... )

    This of course isn't helped by the fact that Goodman no longer makes units themselves, so it's hard to find info online...

    From what I can tell, this line (AE) was supposed to be extra efficient, so it includes ($400+) controllers and blower motors, so I'd rather not go part hunting without knowing it's the right part.

    The motor is original ('97), and I don't believe any other parts have been replaced either. BTW, the motor is a "GE BF06 22BT" (as seen on the motor)

    Thanks!
  • Feb 3, 2008, 01:34 PM
    hvac1000
    Replace the indoor blower motor Capacitor. It is attached by two wires to the motor. Get the numbers off it and the MFD and voltage rate. Then take those numbers to a dealer/parts house. Replace the old with the new and you should be done with the repair.
  • Feb 6, 2008, 04:49 PM
    davidjs
    Quote:

    Originally Posted by hvac1000
    Replace the indoor blower motor Capacitor. It is attached by two wires to the motor. Get the numbers off of it and the MFD and voltage rate. Then take those numbers to a dealer/parts house. Replace the old with the new and you should be done with the repair.

    Here's my problem, there's nothing attached by two wires to the motor.

    The motor (see pictures) has a red/black pair that is run directly from the breaker on the front of the unit. The other wiring bundle runs from the motor to the circuit board pictured. None of the other components (all pictured) look at all what I would know as a capacitor...

    There's a transformer, two fusible links(?), and a relay(?) along with the circuit board (from what I can decipher)...

    Motor: The two large power wires run directly to the breaker
    http://i62.photobucket.com/albums/h1..._4105Small.jpg

    Breaker, transformer in the background (I assume to run the controller)
    http://i62.photobucket.com/albums/h1..._4106Small.jpg

    Fusable links?
    http://i62.photobucket.com/albums/h1..._4108Small.jpg

    Relay? (sorry, couldn't get a great picture)
    http://i62.photobucket.com/albums/h1..._4109Small.jpg

    Closeup of transformer
    http://i62.photobucket.com/albums/h1..._4111Small.jpg


    Any thoughts? Thanks for your help so far
  • Feb 6, 2008, 04:50 PM
    davidjs
    Two of circuit board:
    http://i62.photobucket.com/albums/h1..._4107Small.jpg
    http://i62.photobucket.com/albums/h1..._4112Small.jpg

    (Broken up for 6 picture limit)
  • Feb 6, 2008, 05:37 PM
    hvac1000
    I believe what you have is a DC voltage variable speed board controlled setup now that I see the pictures. You will probably spend more than 500.00 to 600.00 on parts. There is a expensive electronic tool that is made just to check/test those items.
    It is a proven fact that you will not save energy with that setup because when it goes bad you will spend more than you saved for new parts.

    I suggest calling a pro HVAC company that has the proper tools/meters etc to fix it correctly and at the minimum of expense for parts.

    OR




    Do the smart thing. Rip out all blower controls and motor.

    Replace with a conventional 3 or 4 speed motor and wire it up.

    Been there done that and it is a bunch cheaper.

    Here is some not the same brand information about variable speed.

    http://www.nordyne.com/Literature/349c.pdf

    Evergreen ECM Replacement Motors | GE ECM by Regal Beloit | theDealerToolbox.com
  • Feb 6, 2008, 06:06 PM
    davidjs
    Quote:

    Originally Posted by hvac1000
    I believe what you have is a DC voltage variable speed board controlled setup now that I see the pictures. You will probably spend more than 500.00 to 600.00 on parts. There is a expensive electronic tool that is made just to check/test those items.
    It is a proven fact that you will not save energy with that setup because when it goes bad you will spend more than you saved for new parts.

    I suggest calling a pro HVAC company that has the proper tools/meters etc to fix it correctly and at the minimum of expense for parts.

    OR
    Do the smart thing. Rip out all blower controls and motor.

    Replace with a convential 3 or 4 speed motor and wire it up.

    Been there done that and it is a bunch cheaper.

    Here is some not the same brand information about variable speed.

    http://www.nordyne.com/Literature/349c.pdf

    Evergreen ECM Replacement Motors | GE ECM by Regal Beloit | theDealerToolbox.com

    Awesome, thanks for the... good.. news.

    I appreciate the suggestion, I'll probably rewire it, as that will still be cheaper than replacing what I have...
  • Feb 13, 2008, 12:38 AM
    OmahaJoe
    Now for anyone reading this: DO NOT USE GOODMAN. Mine is three months old and not working properly and Park and Sons or Emergency Heating and Repair (same guy) in Omaha Nebraska will not respond. Bad contractor. Bad furnace. If you need a new furnace, do not use Goodman under any circumstances.
  • Feb 13, 2008, 01:03 AM
    hvac1000
    Quote:

    Originally Posted by OmahaJoe
    Now for anyone reading this: DO NOT USE GOODMAN. Mine is three months old and not working properly and Park and Sons or Emergency Heating and Repair (same guy) in Omaha Nebraska will not respond. Bad contractor. Bad furnace. If you need a new furnace, do not use Goodman under any circumstances.


    ((The probem in Goodman won't use dealers, they sell their crap to anyone))


    The factory has a policy and they DO NOT sell to anyone.
    The factory only sells to wholesale houses for the HVAC trade.
    It is the wholesale house or the dealer that is selling to anyone.

    Goodman is just as good as any other equipment if installed correctly.
    The problem is many units are not installed correctly because Joe homeowner bought on off Ebay and installed it himself causing all the problems.