  • Jan 28, 2008, 07:22 PM
    cdinardi28
    Sub pannel grounding
    I put in a 125amp sub panel. I know you can not mix the neutral and ground together in the panel. There are two neutral bars one on each side. My question is can I take the bar out that connects the neutral bars together, use one for grounding and the other for neutral. I ran 3 #2 and 1 #4 for the ground, also a #4 to bond to the cold water. Should I hook up the ground hook to the ground bus bar or leave it off. It say not to connect the grounding hook on sub panels.
  • Jan 29, 2008, 03:37 AM
    tkrussell
    That is exactly the purpose of the jumper bar, if a separate equipment ground bar is needed, remove the jumper bar.

    Probably a GE panel, I think Siemens does the same.

    Use one bar for all white neutrals, and one bar for all green and bare grounds.

    Do not install the green screw provided.