Originally Posted by tsa7man
You stated in your last post.... that the tech "bypassed the limit switch" to keep the unit running...???? This really has me wondering...he bypassed a safety to check a problem. The safety "limit" is doing it's job !!!! Or it is defective !!! The next two questions is simple, as I stated before....have your tech put a thermocouple at the location of the main limit switch that is tripping "open" and read the actual temp that that switch is seeing. It is either tripping to early ( low temp) and defective or it is really sensing a high heat temp, and opens as designed to shut down the gas valve firing. The next question is why is the safety opening ???? It is doing it's job to keep you safe. What can cause this problem, of an over heat condition.....over fired gas valve / burners, dirty air filter, too low of a blower speed ( check the temp rise of unit as per ID plate specs.) time out of circulation fan too short at the end of a heating cycle, heat left in heat exchanger, and upon a new call for heat, the 30 sec. fan on delay causes the heat exchanger to over heat prior to the fan timer starting the circulation blower...= high limit opens now, burners go off...cold air blows.....through your duct work....