Originally Posted by tkrussell
Extension cord?
Installed directly in earth?
Is the cord rated to be direct buried?
I doubt it.
There a several approved methods to install wiring in earth. As previously mentioned, one is to use an electrical cable rated for direct burial, UF, stands for Underground Feeder, usually a thick gray cable with the three separately insulated wires. Or you can use Sch 40 UL listed PVC conduit,UL Listed Steel Galvanized Rigid conduit, and UL Listed Aluminum conduit.
These various methods have their own min depth requirements, however, most can be superseded if the installation is residential, one or two family, is GFI protected, and no more than a 20 amp 120 volt circuit, can be installed at a minimum of 12 inches deep.
And extension cord is not listed as an approved wiring method for being directed buried in earth.
What I have done to cross walkways is to dig the trench on both sides of the walkway, and use a steel rod, conduit, bar and drive thru the dirt to create a bored hole thru the earth, and push the cable or conduit thru the hole, no fuss and no mess with water and mud.
I do sure hope you heed my advice and replace the extension cord with an approved method in earth, imagine your son, daughter, grand kids playing in the lawn, wet from the rain yesterday, and the lawn is energized because you saved a few dollars.