Originally Posted by bolt in blue
Do I need to run 8-3 to update the garage sub box or can I leave it as is with 8-2?
Depends on what this cable is beng used for. If your using this cable for 120 volt loads, with the bare as a neutral and an equipment ground, the only recourse is to install a 3 wire cable with ground.BLK is hot connected to 1 bus bar in sub box. WHT is hot connected to other bus bar in sub box. BARE is neutral/ground connected to ground bar.
You have it hooked up for 120/240 volts. If you have any single pole breakers (120 volt circuits) or any 240 volt circuits that have neutral wires connected to the grounding bus, it is unsafe. 240 volt devices that don't require a neutral (like a heater or some tools) are safe to use in your current configuration. If you intend to use any 120/240 volt devices (240 volt devices that have a neutral) or any pure 120 devices, you will need to convert it to 8/3. If you only need 120 volt devices, you can stick with 8/2, but it will need to be reconfigured.
How can the 8/2 be reconfigured for use with only 120V devices?
Why is it unsafe to have neutral wires grounded to the grounding bus?
What problems could occur from leaving the 8-2?
I was thinking of a 60A sub box. Is that 2 30A 110 lines?
A 60 amp feeder needs to be a minimum of #6 copper wire, using pulled THHN wire thru conduit, or MC cable. If you use Romex, it is only rated 55 amps, but you can use a 60 amp breaker , being the next standard size breaker. In main box, using a double pole 30A breaker - BLK to one hot and RED to other hot. WHT and BARE to ground. In sub box, BLK to one hot bar and RED to other hot bar. WHT to neutral bar and BARE to ground bar that must be added. Using 8-3 wire for this connection. What amp sub box should I purchase?
If you have a double pole 30 amp breaker feeding the box, you can use any box rated for at least 30 amps. The 30 amp double pole breaker will give you 60 amps of power at 120 volts before tripping (both hot legs maxed out at their 30 amp capacity).
Why the need to keep the neutral and ground junctions separate in a sub box?
Short answer....A neutral is considered as current carrying, a ground is only for fault currents, and for safety purposes both are kept separate.
Why are they connected in the main box then?
Neutral is made at the main breaker. The utility provides two hots and a grounded line. In the house, you separate the ground and the current's return path (neutral) for safety. However, because of the way the house and utility connect, there must be exactly one connection between your neutral and the grounding system. This connection must be made at the main breaker. If your main breaker is at your main electrical panel, these will be at the same place. If you have a remote main breaker, you must have isolated ground and neutral in your main panel. All devices elsewhere in the home must isolate ground and neutral. In panels, this usually means purchasing a separate bus bar to be the ground and removing the grounding screw from the included bus bar to make it neutral.