  • Jan 20, 2008, 03:16 PM
    shipshape448
    Furnace air output tempure is low
    I have a Goodman GMP100-3 furnace. Runs constantly. Air temperature coming out of ducts is luke warm. Burners all working fine. All vent pipes checked for leaks. Great air flow just no hot air.
  • Jan 20, 2008, 03:41 PM
    hvac1000
    Check this first >Low gas pressure . The unit is capable of 100,000 BTU input of heat and unless you are trying to heat the outdoors should be more than plenty for a average size house.
  • Jan 21, 2008, 09:30 AM
    shipshape448
    I had my gas pressure check by an HVAC Tech. Guess what, furnace designed to run at 3.5 lbs, input valve set at factory default of 1 lbs. Tech set pressure up and problem was solved.
    Thanks for the tip.
  • Jan 21, 2008, 10:31 AM
    hvac1000
    Yep low pressure is the cause of many problems. Glad you got it fixed.