HVAC Wiring Size for Geothermal units
I've found a number of these type of questions in here and I thought I'd post my own, with what I *think* my solution is.
I have two geothermal units
The first Geo unit has this...
Min CKT Ampacity = 25.6 A
Max HACR = 35 A
The second unit has this...
Min CKT Ampacity = 29.6 A
Max HACR = 45 A
I understand I need to get HACR breakers for the motor start. I'm looking for what size wire I'll need.
For the first unit, the documentation says MIN wire size is a #10 at 60C, but it also says as a subnote "Current carrying capacity of the wire used must not be less than the fuse/breaker size used".
I'm guessing that just means if I use #10 wire, that I should stick a 30 amp breaker in.
For the second units the docs say MIN wire size is again #10. It just seems that with the MIN circuit being 29.6 amps, I should have a bigger breaker there.
I found an article that talked about sizing the protection at 175% of the equipment load current rating (up to 225% if the starting current trips the 175%).
That sounds to me like I can run a 40 amp breaker with #10 wire to that second unit. I think I'll end up running #8 THHN to both units to be on the safe side, but I thought I'd ask.
John
John