-   -   Why do the burners go out before the fan even comes on? (https://www.askmehelpdesk.com/showthread.php?t=173605)

  • Jan 17, 2008, 05:00 PM
    chuckno9
    Why do the burners go out before the fan even comes on?
    The furnace ignites quickly with a blue flame and burns for approximately 2 minutes.
    Then the whole unit stops silent for about a second.
    Then the fan finally comes on after all of this and blows somewhat hot air for approximately
    3 minutes.

    The entire cycle is 2 minutes of burners, then 3 minutes of fan, then off for about 5 minutes.

    It does keep the house at the temp I set the thermostat at. But it seems very inefficient.

    Thermostat is set to 60'


    Thanks for any help

    Chuck Norris
  • Jan 17, 2008, 05:05 PM
    hvac1000
    Hi Chuck Norris. It sounds like your furnace has the Judo Chop Syndrome. LOL

    It could be
    The heat anticipator in the thermostat which will cause the burner to short cycle.
    It could be the fan limit control that has gone out of calibration.
    Keeping a low temp of 60 degrees depending upon the size of the house and the BTU capability of the furnace could trigger a short cycle situation.
  • Jan 18, 2008, 06:39 AM
    therinnaiguy
    Question, If you raise the temperature to say 65, does the unit stay running longer?