Originally Posted by iamgrowler
Quote:
Washers aren't going to be a problem with this valve -- The cartridges are ceramic seated 1/4 turn ones.
This not being a pressure balanced valve is of greater concern, though -- It doesn't meet any of the Plumbing Codes adopted throughout the US -- Since this is a whirlpool tub, you'll need access to the motor, so locate a pressure balancing valve at the motor access hatch and then pipe to the valve from there.
Also, if you don't have the valve yet, I'd wait until you do before placing the tub and hooking up the trap -- A two handled valve fitting in a flat-studded wall is a rarity; Finding out that the stems protrude too far past the finished wall surface upon trim-out can be a real pain in the tukas.
The valve should come with rough-in instructions specifying just how much of the stems should protrude past the finished wall face -- Let these instructions be the deciding factor in whether you need to fur the wall out or not.