  • Jan 11, 2008, 09:06 AM
    Den53nis
    Why does furnace vacuum tube need to be clamped off?
    Lennox gas furnace flame goes out reignites goes out etc. New circuit board installed. Exhaust vent clean. Exhaust blower clean working. Will only continue to burn if vacuum line is disconnected from sensor and clamped off. What is probable cause?
  • Jan 12, 2008, 07:22 AM
    Frdbrkl
    Blockage in condensate trap? Restricted air intake?

    The sensor you are referring to-could it possibly be a pressure switch? (round disc shaped thingamabob with 2 wires and 1 or 2 rubber hoses connected).
  • Jan 12, 2008, 07:47 PM
    Den53nis
    Yes, It is the pressure switch. A New one was tested same problem so that's not it. The vent blower was taken off and checked for blockage all Ok. Air does not appear the problem. What is the Condensate trap??
  • Jan 13, 2008, 07:36 AM
    Frdbrkl
    Quote:

    Originally Posted by Den53nis
    Yes, It is the pressure switch. A New one was tested same problem so thats not it. The vent blower was taken off and checked for blockage all Ok. Air does not appear the problem. What is the Condensate trap????

    A condensated trap is used in high efficiency furnaces to allow the water in the secondary heat exchanger and collector box to drain properly. It's usually plastic, sits in the blower compartment, or right outside the furnace. It typically drains out of 1/2" CPVC pipe or some such into a condensate pump.

    They are not found on 80% efficiency furnaces-just the higher efficiency models. Higher efficiency furnaces extract so much heat out of the vent gasses that the gasses actually reach a temp below dew point in many cases, and condensate is extremely heavy.

    Did the pressure switch have 2 rubber hoses on it or just 1?

    Check for a split in the hose and make sure the unit is sealed tight (for example if the cover is off the burner enclosure, put it back on with its proper seal. If the seal is destroyed, seal it back up with Hi Temp RTV-a red silicone based caulk. It is extremely important to have ALL seals intact on a sealed combustion unit, otherwise pressure switch failure can occur as the negative pressure it needs to engage is not developed when the inducer comes on... it just sucks air through the leak (air, like water, will seek the path of least resistance)
  • Jan 13, 2008, 08:14 AM
    Eric D
    Quote:

    Originally Posted by Den53nis
    The vent blower was taken off and checked for blockage all Ok.

    When the inducer blower was taken apart to inspect, was it sealed properly when being reassembled? If not, you maybe adding to your problems. You have to be sure the seal between the inducer and its mounting is totally sealed as well. Not getting a good seal can cause the pressure differential issue you now have and can allow condensate to leak out of the inducer halves or mounting.

    How old is this furnace? Has the exchanges been inspected?

    Eric D
  • Jan 13, 2008, 06:34 PM
    Den53nis
    The blower is sealed. The hose is not leaking. The furnace is 13 years old. Not high efficiency. Only one hose to the pressure switch. Everything mentioned has been checked, and the same problem exists. The flame is full for 10 seconds with vacuum hose attached and then full shutdown of flame. With hose disconnected and plugged works fine.
  • Jan 13, 2008, 07:07 PM
    T-Top
    Sounds like you have the wrong pressure switch for the job. If you had the right pressure switch for the system and the pressure switch tube was not hooked up the furnace would not work.
  • Jan 14, 2008, 09:45 AM
    Frdbrkl
    Quote:

    Originally Posted by T-Top
    Sounds like you have the wrong pressure switch for the job. If you had the right pressure switch for the system and the pressure switch tube was not hooked up the furnace would not work.

    I agree-sort of. It sounds like the pressure switch is NormallyClosed and proving, but should be NO, and proving on the draft? But all models I've worked on wouldn't fire at all if pressure switch failed on call OR reset (returning to open state). The old carriers with the little inducer board up top... those can be finnicky-but this is a Lennox.

    It's not high efficiency, but has a pressure switch? Hmmm... that's a bit odd in itself. Must be a "chimney friendly" type furnace.

    Honestly, this is starting to get a bit drawn on... and I'm a bit concerned. It may be nothing, but I would certainly have this checked out by a technician. I like to err on the side of safety when it comes to gas and electric. Bad things tend to happen if you don't...
  • Jan 14, 2008, 03:21 PM
    Den53nis
    I have had two separate technicians both of which are stumped. The factory rep has been called. Thanks for all of the posts
  • Jan 14, 2008, 03:48 PM
    Eric D
    Quote:

    Originally Posted by Den53nis
    I have had two separate technicians both of which are stumped. The factory rep has been called. Thanks for all of the posts

    Dennis,

    When you do get it figured out how about a follow-up reply to let us know what you found?

    Thanks,

    Eric D