Carrier 58MSA, code 34, flame proving sensor?
Wanted to know if anyone could help me troubleshoot this problem..
This furnace will not fire up, basically what happens is the igniter lights up, but will shut down after a 5 seconds or so. It will do this three times until it goes into lock down mode for three hours, and then flashes code 34. Please tell me if Im on the right path here.
1. Cleaned flame sensor with scotch brite. NO CHANGE
2. Check to see if I have .5 UAMPS between flame sensor harness and flame sensor. DO NOT HAVE ANY AMPERAGE READING ON THE METER WHEN FURNACE TRIES TO LIGHT?
I noticed that one or both(hard to tell) of the solenoids that control gas flow into the burner are clicking when the igniter is on, so I am assuming gas is going into the burner, although I don't hear any hissing of gas flowing? I also checked to confirm that I have power coming out of the transformer, and I have 28VAC. At this point I don't know if the gas valve is defective, or the computer board?
Thanks for any help guys. Fernando