I was adding a new switch in a 3 gang box in a newly wired kitchen yesterday. I had not yet switched off the breaker and was prepping the wires that were previously roughed in. I pulled out the grounds nutted together for the 2 already hot circuits and felt a tingle... not a big hit but a shock nonetheless. I put a meter on the ground to the neutral a read 112 volts. The box has the following conductors.
1. 12.2 feed from junction box in attic.
2. 3 way switch for 6 fluorescent ceiling cans, black feeder pigtailed to common, white to white on feed, ground to ground feed, 14.3 2 travelers to other switch, white to feed white, grounds all tied together. Works properly.
3. 3 way switch wired same as above for over sink light. Works properly.
4. New circuit is sp swtch feeding undercounter lights.
I removed the nut on the grounds and separated them. The fluorescent can circuit is the one with the hot ground.
Its only hot when the lights are in switched on. When I disconnect the nuetral the lights go out. I did not measure the amperage on the gound. Is this an issue with one of the transformers or a bad connection? What should my next step be?
Thanks,
Jeff